E1.20 RDM (Remote Device Management) Protocol Forums  

Go Back   E1.20 RDM (Remote Device Management) Protocol Forums > RDM Developer Forums > RDM Interpretation Questions

RDM Interpretation Questions Discussion and questions relating to interpreting and understanding the E1.20 RDM Standard.

Reply
 
Thread Tools Search this Thread Display Modes
Old April 30th, 2012   #1
wayne@artisticlicence.com
Task Group Member
 
Join Date: Aug 2006
Posts: 28
Default Sub Device required PIDs

At the plug-fest Bob presented an interesting point: Do Sub Devices need to implement the minimum required PIDs list?
My common sense answer was yes, but review of the document suggests this is not a given.
The root device must support the 'required pids'. Sub Devices must all support the same set of pids which can differ from the root.
However 9.2.3 is open to interpretation. The problem is caused by the phrase 'which additional messages...'. The word additional implies 'in addition to the minimum required pid list' but could also be read to mean 'in addition to the SUPPORTED_PARAMETERS pid.
So there are two possibilities:
a) Sub devices shall at minimum implement the required pid list along with SUPPORTED_PARAMETERS.
b) Sub devices shall at minimum implement the SUPPORTED_PARAMETERS pid.
wayne@artisticlicence.com is offline   Reply With Quote
Old April 30th, 2012   #2
pkleissler
Task Group Member
 
Join Date: Oct 2008
Location: NJ
Posts: 19
Send a message via Skype™ to pkleissler
Default

Yes it is not clear,

My opinion is since section 9.2.3 second paragraph states that SUPPORTED_PARAMETERS list can be different from that of the root device, a sub device only supports what it reports in response to a get SUPPORTED_PARAMETERS message. The required discovery PIDs would also not make much sense for a sub device.

Paul
pkleissler is offline   Reply With Quote
Old April 30th, 2012   #3
sblair
Administrator
 
Join Date: Feb 2006
Posts: 441
Send a message via AIM to sblair Send a message via MSN to sblair
Default

It was never expected that the minimum supported PID's list applied to sub-devices. In fact if you look at the list of PID's in the minimum supported list most of them don't make any sense in the context of a dimmer rack implementing sub-devices which was the straw man model we most used.

It was intended that all the PID's implemented by Sub-Devices be reported using the SUPPORTED_PARAMETERS message.

I agree that the text could be a bit clearer on this.
__________________
Scott M. Blair
RDM Protocol Forums Admin
sblair is offline   Reply With Quote
Old April 30th, 2012   #4
wayne@artisticlicence.com
Task Group Member
 
Join Date: Aug 2006
Posts: 28
Default

So the answer is that SUPPORTED_PARAMETERS is the only pid mandated for a sub-device.
wayne@artisticlicence.com is offline   Reply With Quote
Old April 30th, 2012   #5
sblair
Administrator
 
Join Date: Feb 2006
Posts: 441
Send a message via AIM to sblair Send a message via MSN to sblair
Default

Quote:
Originally Posted by wayne@artisticlicence.com View Post
So the answer is that SUPPORTED_PARAMETERS is the only pid mandated for a sub-device.
That is my view and belief of what the intent was. There really isn't any other interpretation of what is written that makes sense to me.
__________________
Scott M. Blair
RDM Protocol Forums Admin
sblair is offline   Reply With Quote
Old April 30th, 2012   #6
wayne@artisticlicence.com
Task Group Member
 
Join Date: Aug 2006
Posts: 28
Default

Great - works for me.
wayne@artisticlicence.com is offline   Reply With Quote
Old April 30th, 2012   #7
ericthegeek
Task Group Member
 
Join Date: Aug 2008
Posts: 390
Default

I've posted my thoughts on Sub-Devices before in this thread:
http://rdmprotocol.org/forums/showpo...24&postcount=6

Here's what I wrote:
Quote:
There's no mandate that sub-devices have to support all of the other required PIDs. Per section 9.2.3, the only PID that a sub-device must support is SUPPORTED_PARAMETERS. In fact, the discovery PIDs are explicity root-only, thus are can't be mandatory for the sub-devices.

PIDs like DEVICE_INFO and IDENTIFY_DEVICE might be valuable in many cases, and it can't hurt to support SOFTWARE_VERSION_LABEL. If the sub-devices have separate software, report that version number for SOFTWARE_VERSION_LABEL, or just report the same version as the root.

As I've said before, I think DEVICE_INFO is effectively required (even though it's not stated in the standard) since there is some information in DEVICE_INFO that isn't available anywhere else. (Such as sensor count and the DMX Footprint for a device that doesn't support personalities.)
ericthegeek is offline   Reply With Quote
Old May 1st, 2012   #8
wayne@artisticlicence.com
Task Group Member
 
Join Date: Aug 2006
Posts: 28
Default

Thanks Eric. I'd agree on DEVICE_INFO - not much point having a sub-device where you can't get start and foot!
wayne@artisticlicence.com is offline   Reply With Quote
Old May 1st, 2012   #9
ericthegeek
Task Group Member
 
Join Date: Aug 2008
Posts: 390
Default

On other factor that's come up in newer discussions is that Sub-Devices should list all of their PIDs in SUPPORTED_PARAMETERS, even PIDs like DEVICE_INFO that are mandatory and not listed in SUPPORTED_PARAMETERS for root devices.

The gray area is whether sub-devices should include SUPPORTED_PARAMETERS in the list returned by GET SUPPORTED_PARAMETERS. My opinion is *no* since SUPPORTED_PARAMETERS is explicitly required by section 9.2.3.
ericthegeek is offline   Reply With Quote
Old May 1st, 2012   #10
sblair
Administrator
 
Join Date: Feb 2006
Posts: 441
Send a message via AIM to sblair Send a message via MSN to sblair
Default

Quote:
Originally Posted by ericthegeek View Post
The gray area is whether sub-devices should include SUPPORTED_PARAMETERS in the list returned by GET SUPPORTED_PARAMETERS. My opinion is *no* since SUPPORTED_PARAMETERS is explicitly required by section 9.2.3.
Correct. The list for SUPPORTED_PARAMETERS from the Root device is for the root device only and should NOT include the sub-device. Likewise sending SUPPORTED_PARAMETERS to the sub-device should give you the list for sub-devices only.
__________________
Scott M. Blair
RDM Protocol Forums Admin
sblair is offline   Reply With Quote
Old May 1st, 2012   #11
ericthegeek
Task Group Member
 
Join Date: Aug 2008
Posts: 390
Default

Scott, you and I are talking about something different.

On the root device, the standard says that the list of PIDs returned by GET SUPPORTED_PARAMETERS does not include the mandatory PIDs. For example, the list returned by the root device should not include SOFTWARE_VERSION_LABEL since SOFTWARE_VERSION_LABEL is required. This, a controller would normally not expect to see SOFTWARE_VERSION_LABEL in the list of supported parameters.

But, the same rule does not apply to sub-devices. When you send a GET SUPPORTED_PARAMETERS to a sub-device, the list of PIDs should include SOFTWARE_VERSION_LABEL. Thus, when getting the PID list from a sub-device, a controller can expect to see PIDs included in the list that would never be returned by a properly implemented root device.
ericthegeek is offline   Reply With Quote
Old May 1st, 2012   #12
sblair
Administrator
 
Join Date: Feb 2006
Posts: 441
Send a message via AIM to sblair Send a message via MSN to sblair
Default

Eric,

Agreed!
__________________
Scott M. Blair
RDM Protocol Forums Admin
sblair is offline   Reply With Quote
Old May 2nd, 2012   #13
wayne@artisticlicence.com
Task Group Member
 
Join Date: Aug 2006
Posts: 28
Default

Eric, I also agree although I have ensured our implementation is tolerant of responders including or excluding mandated pids, root or sub-device.
wayne@artisticlicence.com is offline   Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Required handling of sequences of RDM broadcast cmds eldoMS RDM Timing Discussion 9 August 23rd, 2011 09:40 AM
Is there a minimum required PID list for sub-devices? p_richart RDM Interpretation Questions 4 November 7th, 2008 01:04 PM


All times are GMT -6. The time now is 02:13 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2026, vBulletin Solutions, Inc.